Landscape Lighting Wiring

8/19/2005 3:36:11 PM
Mike

8/19/2005 3:36:11 PM
I'm planning to run 12-2 home run wires from a 600W multi-tap transformer to six hubs. The hubs will be located between 10' to 100' from the transformer. I then want to run 25' of 16-2 wire to three or four fixtures from each hub. Each fixture will have an MR-16 20W bulb and already have approximately 36" of 18-2 lead wire pre-attached. Can I mix these three sizes of wire and should this approach prevent voltage drop? Alternatively, I could use the T method of wiring each group of three or four fixtures. I understand that with a group of four fixtures, I can hook up the 12-2 home run wire to a T connector placed between the middle two lights and then continue to run the 12-2 wire to both fixtures on either side of the T connector. But,how do you hook up the T method for a group of three lights? Do you wire the home run wire with the two wires running to either side and with the lead wire from the middle fixture?

  Add to Favorites

re: Landscape Lighting Wiring

Posted: 8/19/2005 9:47:15 PM

EXPERT

8/19/2005 9:47:15 PM
I would would stick with 12/2 wire for the secondary feeds and 10/2 for your home runs back to the transformer.  I like to never put more than 100 watts on 100 feet of wire to just be safe.  With the 10/2 you can double that total.  If you use 12/2 DIRECT BURIAL CABLE on the secondary runs as mentioned, you can use the supplied CONNECTORS to attach each 18/2 fixture lead to the cable.  Why don't you check out our handy POWER CABLE CALCULATOR for more information.

  Add to Favorites
1-800-239-2939